Hi,
I got a question relate to ASHRAE 90.1-2010 Wall Construction from the EP Construction Library. I found out that the U-value from the EP Library does not match with ASHRAE 90.1-2010 exactly (for example, for Climate zone 1 Extmass Wall, EP Library offers U=0.649, whereas ASHRAE requires max 0.580 using IP Units).
The other question is that is the library updated to ASHRAE 20.1-2013?
Thanks!
Best,
Rufei
Tags:
Replies are closed for this discussion.
Hi Rufei,
Thanks for reporting this. The libraries are from OpenStudio standards.
https://github.com/NREL/openstudio-standards/blob/master/openstudio...
You can check the details in GoogleSheets. Let us know if we're making any mistakes.
Do you mean ASHRAE 90.1-2013? Here are the standards that are available. We can update the libraries for the next release.
Mostapha
Hi Chris,
Thanks for your detailed explanation, that makes a lot of sense. Now I understand why the EP Construction has a higher U-value than the code. But I got one question for ASHRAE 90.1-2010 Extwall Mass Climate zone 7-8, the U-value is 0.054, but the code is 0.071, should I change R-16.84 to R-11.2 in order to make a U-value of 0.075?
Best,
Rufei
Hi Mostapha,
Thanks for your reply! I will take a look at this.
Best,
Rufei